Old 06-01-2008, 02:13 AM   #1
HoosierDaddy
Senior Member
 
HoosierDaddy's Avatar
 
Join Date: Mar 2006
Location: Indiana
Posts: 424
Unhappy Arrgh help!!!

12.5 kw kohler/perkins 1978 Newell. When I tried to start the generator this spring it just would not fire. I have been chasing fuel problems for 2 weeks now. Even R/B the lift pump. Today I'm finally getting some fuel dripping from the injector lines but then the generator quits cranking. Its dead... apparently no 12v at the no.3 terminal on the control box circuit board (the power that goes to the remote switch at the instrument panel) The fuse on the back of that panel in the control box checks OK...it has 12v in and out. If I manually trip the relay (CR) on the panel it will crank. Is there another fuse that I'm missing? Thanks, Dean
__________________

__________________
1993 Newell 45'#316, 1976 Trans Am 455, 1967 GTO, 1953 Chevrolet 3105 (panel truck),1952 Chevrolet 3600,1969 Airstream Overlander. Always fixing something!
HoosierDaddy is offline   Reply With Quote
Old 06-01-2008, 02:25 PM   #2
fulltiming
Senior Member
 
fulltiming's Avatar
 
Join Date: Feb 2006
Location: Texas
Posts: 1,558
Default

Dean, the manual lists two fuses: a 10 amp fuse on the relay controller (typically next to the Preheat/Prime Switch and an 8 amp fuse located in the end bracket assembly or junction box. The engine should crank, but not start if the 8 amp fuse is blown. If the 10 amp fuse is blown, the engine will not crank. The junction box is the large box directly behind the fuel filter and the end bracket assembly contains the connector and the automatic voltage regulator near the junction box.

You might replace the 10 amp fuse even though it is showing voltage across it. Sometimes a fuse element will develop a slight fracture and show no load voltage but will fail to pass load current.

Looking at the wiring schematic, power from the battery goes directly to the starter solenoid, then from the starter solenoid to the air heater relay, then into terminal 1 on the connector at the rear of the controller, then to the connector strip (position P, next to 1) inside the controller then to the 10 amp fuse. You might want to confirm that the connections are good and clean at the solenoid, the air heater relay and that the contacts on the connector strip in the controller on both sides of terminal P are clean and tight. You could try a jumper from the each side of the rear of the 10 amp fuse to the trigger on the starter solenoid to verify that you have power coming into the controller and to verify that the fuse is good.

You should also be getting more than just a little fuel dripping from the injector lines.

Let us know what you find and we will continue to track down your problem.
__________________

__________________
Michael and Georgia Day
1992 Newell 43.5' #281
8V92 DDEC-2, HT740
PT Cruiser GT with Remco Transmission Pump
https://newellowner.com/newell-photos/
fulltiming is offline   Reply With Quote
Old 06-01-2008, 02:29 PM   #3
fulltiming
Senior Member
 
fulltiming's Avatar
 
Join Date: Feb 2006
Location: Texas
Posts: 1,558
Default

As a further thought, if you can start by jumping from the fused side of the fuse unit to the trigger on the starter relay, the potentially the ground is being broken by a defective low oil pressure switch or a defective high temperature switch.
__________________
Michael and Georgia Day
1992 Newell 43.5' #281
8V92 DDEC-2, HT740
PT Cruiser GT with Remco Transmission Pump
https://newellowner.com/newell-photos/
fulltiming is offline   Reply With Quote
Old 06-11-2008, 02:54 AM   #4
HoosierDaddy
Senior Member
 
HoosierDaddy's Avatar
 
Join Date: Mar 2006
Location: Indiana
Posts: 424
Default Follow-up

Here's what we found: A small piece of rubber had lodged in the fuel line between the lift pump and the filter....causing the initial fuel starvation. After repeated cranking the starting system went dead. There is a re-set switch on the back side of the control box which is not normally visible. After resetting the generator would crank again. We put new rubber seals on the fuel lines and installed a new lift pump and starter motor and it's good to go. (Actually feeling my way through all this was much more involved than I can describe!!!)
Thanks for the help, Fulltiming!!!
Dean
__________________
1993 Newell 45'#316, 1976 Trans Am 455, 1967 GTO, 1953 Chevrolet 3105 (panel truck),1952 Chevrolet 3600,1969 Airstream Overlander. Always fixing something!
HoosierDaddy is offline   Reply With Quote
Old 06-11-2008, 03:58 AM   #5
fulltiming
Senior Member
 
fulltiming's Avatar
 
Join Date: Feb 2006
Location: Texas
Posts: 1,558
Default

Glad you got to the root of the problem. Thanks for updating us. I will remember to add those fuel lines to my list of needed updates.
__________________
Michael and Georgia Day
1992 Newell 43.5' #281
8V92 DDEC-2, HT740
PT Cruiser GT with Remco Transmission Pump
https://newellowner.com/newell-photos/
fulltiming is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Newell Coach Corporation or any of its affiliates. This is an independent, unofficial site.


All times are GMT. The time now is 12:36 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
×