Default Dometic Basement Air/// basement unit not working

One of my basement airs was not blowing cold air. The fan in the coach was running but no cold air. The unit in the basement does not come on. I do not have voltage at the black and white 120 service at the basement unit. The breaker is not tripped in the breaker box in the rear of the coach.

Any ideas on where to start? It's the front one if that makes any difference.

The lovely bride says this in numero uno priority. Gotta have AC in Tejas.
__________________

__________________
Richard Rhonda Ty and Alex Entrekin
1995 Newell # 390 DD Series 60, Allison World Trans
Subaru Outback toad
CoMotion Tandem
Often wrong, but seldom in doubt
Rhonda's chronicle https://wersquared.wordpress.com/
Richard and Rhonda is offline   Reply With Quote
Old 03-10-2008, 03:11 PM   #2
Richard and Rhonda
Senior Member
 
Richard and Rhonda's Avatar
 
Join Date: Oct 2007
Location: Huntington WV
Posts: 1,041
Default

This is what I have learned so far, just in case you have to investigate a similar problem in your coach.

The main control board for the Dometic units is usually located in close proximity to the evaporator (the unit inside the coach) For my front unit, the evaporator is right by the door, underneath the kitchen counter. When I removed some of the internal pieces of the cabinet, I found a small box with the control board inside. On the control board is a relay the provides power to the condenser unit. This relay is not "making". When I bypass the relay and hardwire power to the condenser, it works as it should.

Here are some other useful bits of info.

My Dometic systems are filled with R22. I took these measurements at about 55 degrees ambient. The static pressure in all three units was about 90 psi. When running the high side was about 150 and the low side about 45.

I have to find a replacement board now.
__________________

__________________
Richard Rhonda Ty and Alex Entrekin
1995 Newell # 390 DD Series 60, Allison World Trans
Subaru Outback toad
CoMotion Tandem
Often wrong, but seldom in doubt
Rhonda's chronicle https://wersquared.wordpress.com/
Richard and Rhonda is offline   Reply With Quote
Old 03-10-2008, 03:46 PM   #3
fulltiming
Senior Member
 
fulltiming's Avatar
 
Join Date: Feb 2006
Location: Texas
Posts: 1,558
Default

Richard, trying to find a replacement board may be a bit of a chore since Dometic doesn't make our type of units any longer according to the folks at Newell. You may be able to find someone that is good at electronic troubleshooting that can go through your board and locate the defective components and replace them. I have found a guy in Yuma, AZ that was able to get one of my basement A/C's working after several others had failed.

I understand that you have determined that one or multiple relays on your board are fried. Hopefully, replacing those relays with good ones will solve your problem.
__________________
Michael and Georgia Day
1992 Newell 43.5' #281
8V92 DDEC-2, HT740
PT Cruiser GT with Remco Transmission Pump
https://newellowner.com/newell-photos/
fulltiming is offline   Reply With Quote
Old 03-10-2008, 03:54 PM   #4
Richard and Rhonda
Senior Member
 
Richard and Rhonda's Avatar
 
Join Date: Oct 2007
Location: Huntington WV
Posts: 1,041
Default

Yep, you're right. Obsolete, no longer available. Dometic says the only fix from their end is a replacement control box and thermostat. About $200.00. I think I will try some new relays first and see if that works.

For info the new control box is Dometic part no 3109226.005 and the thermostat 3109228.001
__________________
Richard Rhonda Ty and Alex Entrekin
1995 Newell # 390 DD Series 60, Allison World Trans
Subaru Outback toad
CoMotion Tandem
Often wrong, but seldom in doubt
Rhonda's chronicle https://wersquared.wordpress.com/
Richard and Rhonda is offline   Reply With Quote
Old 03-10-2008, 04:01 PM   #5
fulltiming
Senior Member
 
fulltiming's Avatar
 
Join Date: Feb 2006
Location: Texas
Posts: 1,558
Default

Thanks for the part numbers Richard. I will add that to my parts list information. $200 is cheap compared with replacing the entire unit with a new 14K BTU Dometic CruisAir unit although I do like the digital thermostats available with the CruisAir.
__________________
Michael and Georgia Day
1992 Newell 43.5' #281
8V92 DDEC-2, HT740
PT Cruiser GT with Remco Transmission Pump
https://newellowner.com/newell-photos/
fulltiming is offline   Reply With Quote
Old 03-22-2008, 12:53 AM   #6
Richard and Rhonda
Senior Member
 
Richard and Rhonda's Avatar
 
Join Date: Oct 2007
Location: Huntington WV
Posts: 1,041
Default

I determined the relay on the board was bad. Ordered one for about 7 bucks, and replaced it. Works great now.

I pulled the relay part number off the top of the relay, googled it, and ordered from an online components supplier.

If you haven't replaced thingies on a printed circuit board, it really isn't that hard. You need a small soldering iron, and solder wick. Solder wick is braided copper wire. You use it to wick the solder off the joint. That way the component will come right off the board. Put the new piece in, hit it with the iron and a little solder, and you are in business.
__________________
Richard Rhonda Ty and Alex Entrekin
1995 Newell # 390 DD Series 60, Allison World Trans
Subaru Outback toad
CoMotion Tandem
Often wrong, but seldom in doubt
Rhonda's chronicle https://wersquared.wordpress.com/
Richard and Rhonda is offline   Reply With Quote
Old 03-22-2008, 01:04 PM   #7
larryweikart
Senior Member
 
larryweikart's Avatar
 
Join Date: Feb 2006
Location: Iyopawa Island, Mi. (sometimes)
Posts: 421
Default

There is a gentleman located in Elkhart In. who was with Dometic for many years before starting his own business. He has a wealth of knowledge about the a/c system used on the Newell and has helped me thru my problems. The split air system used in the 90's is obsolete and creates a major problem if it should ever need to be replaced. Thankfully, Newell has located a source for replacing the compressor if needed as one of mine did. This mans name is Dave Holmes, "Holmes on Wheels" phone #574-266-1586. Definitely a number to keep on your cell. :roll: javascript:emoticon('')
__________________
1994 Newell #365 w/Corvette, 2002 streetrod 34 ford golf cart, 2009 Smart Car, 1958 Century Coronado, 1965 Cruisers Inc, CAR & BOAT CRAZY! LOVE OUR NEWELL!
larryweikart is offline   Reply With Quote
Old 03-22-2008, 01:07 PM   #8
larryweikart
Senior Member
 
larryweikart's Avatar
 
Join Date: Feb 2006
Location: Iyopawa Island, Mi. (sometimes)
Posts: 421
Default

There is a gentleman located in Elkhart In. who was with Dometic for many years before starting his own business. He has a wealth of knowledge about the a/c system used on the Newell and has helped me thru my problems. The split air system used in the 90's is obsolete and creates a major problem if it should ever need to be replaced. Thankfully, Newell has located a source for replacing the compressor if needed as one of mine did. This mans name is Dave Holmes, "Holmes on Wheels" phone #574-266-1586. Definitely a number to keep on your cell. :roll'')
__________________
1994 Newell #365 w/Corvette, 2002 streetrod 34 ford golf cart, 2009 Smart Car, 1958 Century Coronado, 1965 Cruisers Inc, CAR & BOAT CRAZY! LOVE OUR NEWELL!
larryweikart is offline   Reply With Quote
Old 03-23-2008, 02:59 AM   #9
Richard and Rhonda
Senior Member
 
Richard and Rhonda's Avatar
 
Join Date: Oct 2007
Location: Huntington WV
Posts: 1,041
Default

Thanks Larry, great post!!!!

Just for info, do you remember the source and part no for the compressor? And when you replaced the compressor, did you stay with R22 or convert to R135a?
__________________
Richard Rhonda Ty and Alex Entrekin
1995 Newell # 390 DD Series 60, Allison World Trans
Subaru Outback toad
CoMotion Tandem
Often wrong, but seldom in doubt
Rhonda's chronicle https://wersquared.wordpress.com/
Richard and Rhonda is offline   Reply With Quote
Old 03-29-2008, 12:47 PM   #10
larryweikart
Senior Member
 
larryweikart's Avatar
 
Join Date: Feb 2006
Location: Iyopawa Island, Mi. (sometimes)
Posts: 421
Default

Sorry for the delay Richard, been at a race track without internet service. Must get a dish to correct this problem. I do not have that info with me but can send it to you in 2 weeks when I get home. I went to Newell factory and actually drove to Joplin to get the compressor which they then installed. I have not changed from R22. All 4 airs are now working properly. I also purchased an extra compressor just in case they become difficult to locate.
__________________

__________________
1994 Newell #365 w/Corvette, 2002 streetrod 34 ford golf cart, 2009 Smart Car, 1958 Century Coronado, 1965 Cruisers Inc, CAR & BOAT CRAZY! LOVE OUR NEWELL!
larryweikart is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Newell Coach Corporation or any of its affiliates. This is an independent, unofficial site.


All times are GMT. The time now is 02:58 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
×