Automatic Transfer Switch
After burning up TWO Automatic Transfer Switches in succession under Newell warranty as I was within the 24 months warranty that comes with buying a quailfying coach from Newell, they suggested I ALWAYS turn off the A/C before changing from shoreline to genset or vice versa. Five years later, still no problems. Just a little procedure to remember.
The explanation was that so much power is drawn by the A/C systems (my 2001 coach has two basement air units) that changing power sources with the A/C running will pull so much power through the switch that there could be arcing that burns the contact surfaces.
__________________
|
|
|
09-23-2011, 03:08 PM
|
#2
|
Senior Member
Join Date: Jan 2010
Posts: 346
|
Barry,
That is excellent advice and I might add there are a few other big loads I would be sure are off before I made the switch:
Dryer
Stove Top
AquaHot Electric
Take care,
Russ
__________________
|
|
|
09-23-2011, 03:40 PM
|
#3
|
Senior Member
Join Date: Feb 2010
Posts: 433
|
Learned the hard way on my previous coach---roof airs too.
__________________
Steve
Newell
|
|
|
09-24-2011, 12:24 AM
|
#4
|
Senior Member
Join Date: Oct 2007
Location: Huntington WV
Posts: 1,041
|
Been there done that. I had the microwave on and fired the genny cause the campground voltage was low.
Burned out the coil in the transfer switch. The shore power would release, and the genny was trying to pull in the other side.
You know me, too cheap to replace the ATS, so I found an exact replacement coil for about 30 bucks.
So..... I kill everything now when transferring power sources. The first mate is trained to shut it down when I unplug and fire the genny.
__________________
Richard Rhonda Ty and Alex Entrekin
1995 Newell # 390 DD Series 60, Allison World Trans
Subaru Outback toad
CoMotion Tandem
Often wrong, but seldom in doubt
Rhonda's chronicle https://wersquared.wordpress.com/
|
|
|
11-18-2011, 04:36 PM
|
#5
|
Member
Join Date: Feb 2008
Posts: 19
|
hi I'm having a problem with my transfere switch. I guess the problem is with me. I switched from shore power to Gen power while the generator was running. the switch seems to be locked in gen mode, and I cannot move the switch. I have a 84 newell.thanks in advance, leobess
|
|
|
|