Originally Posted by Viva Las Vegas JDR View Post
RV 50A service is 2 legs of 120VAC, usually wired so there is 240VAC across the 2 hot legs. It's not 240VAC service, as both legs are referenced to a neutral. It's possible to wire an RV 50A outlet so the 2 hot legs are in phase and measure 0 between them, but this won't matter unless the RV has any 240VAC appliances.
Is that true? If the two legs are on the same120v phase and the system had a full load, wouldn't the neutral wire have to carry 100 amps? I don't think the wire is rated for that much current.