Old 12-26-2012, 05:14 PM   #1
Newell Attack
Senior Member
 
Newell Attack's Avatar
 
Join Date: Jan 2006
Location: Prescott Valley, AZ
Posts: 237
Exclamation Kohler 12.5KW Generator Stops after 15 Seconds

I need some help. Kohler 12.5KW Generator. Will start then stop after about 15 seconds. I can start again my manually closing the choke but will soon sputter out and die. Have to let set about 2 min. and can restart.

Thanks,

Jeff
__________________
1978 39 FT. Newell Classic

Jeff & Leann Shackly
Newell Attack is offline   Reply With Quote
Old 12-26-2012, 05:36 PM   #2
MrE
Senior Member
 
MrE's Avatar
 
Join Date: May 2012
Location: Boise Idaho
Posts: 719
Default

Sounds like a fuel issue, clogged filter or water. I would check the air filter and clean/replace as necessary and replace the fuel filter. If you have a water separator I would maintain it also. Good idea to fill your new fuel filter with fuel prior to installing so that you don't lose prime.
__________________
Jon & Chris Everton
1986 40' Dog House #86
0 hp 8V92 Allison HT740
Soon to be 500hp ISM with ZF 6 Speed
MrE is offline   Reply With Quote
Old 12-27-2012, 12:56 PM   #3
HoosierDaddy
Senior Member
 
HoosierDaddy's Avatar
 
Join Date: Mar 2006
Location: Indiana
Posts: 424
Default

I agree with Jon... Also check fuel shut-off solenoid. That is on right side of engine connected to the rod that leads to the fuel pump shut-off valve. It may appear to be a "choke". If solenoid is weak it will shut off fuel to pump. Check for proper voltage to solenoid before replacing.
__________________
1993 Newell 45'#316, 1976 Trans Am 455, 1967 GTO, 1953 Chevrolet 3105 (panel truck),1952 Chevrolet 3600,1969 Airstream Overlander. Always fixing something!
HoosierDaddy is offline   Reply With Quote
Old 12-27-2012, 02:45 PM   #4
77newell
Senior Member
 
Join Date: May 2008
Location: Just North of Detroit, a surprizingly great city
Posts: 380
Default

If after changing the filter it continues to behave badly let us know. It sounds like restricted fuel flow though the response to the "choke" is a bit mystifying as diesels don't have chokes like you used to see on gas engines so if the gen is indeed diesel you are moving something else the responders above have guessed at what you moved but we can't know for sure until you describe its location on the engine.

Now, if a fuel filter fixes the immediate problem you may still have a future problem in waiting. How long since you last changed the filter, if it isn't that long you may have an algae problem and you will at a minimum want to treat the tank with algicide and expect to consume a bunch of filters until the "infection" is gone.
__________________
Jon and Alie Kabbe
Started with 77 Coach
Now have 39' 93 coach
2007 civic toad
77newell is offline   Reply With Quote
Old 12-27-2012, 03:15 PM   #5
express1
Senior Member
 
express1's Avatar
 
Join Date: Mar 2009
Location: south louisiana
Posts: 654
Default

The little I know, sounds like common issue. Sucking air!
express1 is offline   Reply With Quote
Old 12-28-2012, 09:24 PM   #6
ccjohnson
Senior Member
 
ccjohnson's Avatar
 
Join Date: Jan 2012
Location: Southwest NM
Posts: 346
Default

Possibly the fire extinguisher safety shut-off? It is is designed to prevent generator from running if the charge on automatic fire extinguisher is low.
__________________
Clint C. Johnson / Fran Balm
Coach 289 '92 42'6" 8V92 Hybrid
Several Toads:
XL-7
F-350 4X4 Crewcab
F-250 4X4 Crewcab
ccjohnson is offline   Reply With Quote
Old 12-28-2012, 11:01 PM   #7
Chester B. Stone, Jr.
Senior Member
 
Chester B. Stone, Jr.'s Avatar
 
Join Date: Oct 2011
Location: Sam Carlos, Sonora, Mex.
Posts: 407
Default

Clint, I would be interested in more information on the auto fire extinguisher shutting down the generator.
__________________
2001 Newell #579
tow a 2011 Honda Odyssey
1935 Mercedes 500K replica
Chester B. Stone, Jr. is offline   Reply With Quote
Old 12-29-2012, 12:56 AM   #8
ccjohnson
Senior Member
 
ccjohnson's Avatar
 
Join Date: Jan 2012
Location: Southwest NM
Posts: 346
Default

It happened to us one night in Ruidoso, NM. Called Newell first thing in the morning & was able to get a temporary work around. There is a 4 hole "freezer" plug up by the control head on the generator. If i recall correctly, the test procedure I used was to unlpug the 4way plug (one of the wires will go to the fuel solenoid), next I ran a good 12V+ jumper wire to the fuel solenoid. When the generator started & stayed running I rigged a short jumper at the plug to get by. I would caution it was just a temporary fix until we could get to Newll to replace fire extinguisher. I hate to defeat a safety system that is designed to save my life & property! Be sure to keep a close eye on oil pressure water temp on generator as you have defeated the safety shut downs with this by-pass. The problem with the fire extinguisher was just age as far as we were able to tell which resulted in a very gradual loss of pressure over the years until it reched the point of shut down mode.
__________________
Clint C. Johnson / Fran Balm
Coach 289 '92 42'6" 8V92 Hybrid
Several Toads:
XL-7
F-350 4X4 Crewcab
F-250 4X4 Crewcab
ccjohnson is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
barrett-jackson hits the road in luxury coach - is it a newell coach? Maxwell55 General Luxury Coach Discussion 1 01-10-2013 11:44 PM
Ocotillo Wells chockwald Life on the Road | Livin' in Luxury 6 12-07-2008 05:43 PM
Rain and flooding Mikeh Life on the Road | Livin' in Luxury 4 07-06-2007 04:22 PM
79 Newell air leveling? Rich Farr Running Gear, Brakes, Tires, Chassis and Pneumatic Systems 1 03-02-2002 03:38 PM

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Newell Coach Corporation or any of its affiliates. This is an independent, unofficial site.


All times are GMT. The time now is 06:36 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
×