When turning the thermostat on heat, the fan turns on and air comes out of the fvents. It's not warm air, but it's air. It never heats up and after about 5 minutes it turns off and doesn't turn on again until you turn the switch off and then back on the thermostat. Is there a pilot light I'm missing? There is propane, all of the appliances light up just fine.

Thanks in advance for your help!!!
__________________

__________________
1989 Newell Coach 40ft Classic
Lou Placentia is offline   Reply With Quote
Old 01-14-2013, 02:38 PM   #2
MrE
Senior Member
 
MrE's Avatar
 
Join Date: May 2012
Location: Boise Idaho
Posts: 719
Default

Lou, here is a link to a thread discussing a similar issue. There is also a link in the thread to the owners manual. http://www.luxurycoachlifestyle.com/...n-furnace.html
__________________

__________________
Jon & Chris Everton
1986 40' Dog House #86
0 hp 8V92 Allison HT740
Soon to be 500hp ISM with ZF 6 Speed
MrE is offline   Reply With Quote
Old 01-14-2013, 06:50 PM   #3
The Newell
Senior Member
 
The Newell's Avatar
 
Join Date: Dec 2005
Location: Southern California
Posts: 1,018
Default

It sounds to me like a critter problem. Maybe dirt dobbers. It could be them, or spiders making nests in your burner or vents. If you get close to the heater unit, can you hear a "clicking" sound (the ignitor trying to light the burner)? If so, and it does not light, critters somewhere would be my diagnosis.
__________________
1976 Newell Classic (Sold)

Home Base: Riverside, CA

If anyone needs my contact info private message me and I will send it to you.

-Joseph-
The Newell is offline   Reply With Quote
Old 01-14-2013, 11:49 PM   #4
PIExpress
Member
 
PIExpress's Avatar
 
Join Date: Sep 2009
Posts: 53
Default

Your furnace is not igniting. The fans come on first, but if no ignition occurs they will eventually shut off, as yours do. Ignition is electronic, not by pilot light. Low voltage to the furnace could be the cause
__________________
1980 Newell Coach
PIExpress is offline   Reply With Quote
Old 01-15-2013, 04:31 PM   #5
NewellCrazy
Senior Member
 
NewellCrazy's Avatar
 
Join Date: Sep 2006
Location: Sugarland, TX or Salida,CO
Posts: 1,867
Default

There are several possible issues

Here is the sequence of events that SHOULD happen

Thermostat calls for heat, Blower turns on and air begins to move,
As the air moves a SAIL SWITCH inside the furnace senses air flow and closes
Burner lights and air gets warm... As rig heats up Thermostat signals "Hot enough" and burner shuts down
Fan may continue to run for a few seconds or may shut down promptly

Possible issues are MOSTLY with the air flow.. If something has "nested" in an air duct, air flow will be reduced. If you have a throw rug or other object blocking more than one air vent, air flow may be reduced, if there is "Crud" build up in the ducts, air flow may be reduced, if a duct has collapsed,, Air flow may be reduced

If the batteries are low, the blower can not come up to speed and air flow is reduced

if the blower is worn out.. Likewise

If air flow is reduced the sail switch won't sail closed and thus the burner won't light

To test.. You need to check the state of the sail switch.. I am afraid I can not help much there as I've never actually looked at the control board for my heater.

Next.. We have burner issues.. There is a spider that loves to next in gas jets, clogging the jet and preventing ignition. I've cleaned quite a few spider nests out of assorted gas jets.. NOT, so for, on the RV, but on other stuff.

Next we have the ignition point (Assuming it is and ESI system) you should HEAR it sparking, and if you can observe the points you should SEE It sparking. I have seen points way, way, way out of adjustment (Reset them and years later that furnace was still functioning properly)

Next we have the thermocouple (Flame sensor) if it's bad it signals the control board "NO FLAME, Safety shut down"

Now we have the control board and last the gas solenoid

And that is just about the list for the symptom (no heat) you have

Most of 'em are easy to fix, and with the exception of the control board and solenoid, not too expensive
__________________
Sean

If Ain't a Newell, It Ain't Wurt Oonin!
NewellCrazy is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Utah State Listings Neweller Southwest 0 08-31-2012 08:19 AM
Xantrex or Outback Inverters Dom Ferris Charging Systems, Electrical & Solar 8 08-22-2012 12:28 PM
Grohe Ladylux kitchen faucet folivier Coach Plumbing Component Data & Diagrams 0 07-11-2012 11:28 PM
Strange Stuff express1 Wine-n-Dine, Events, Rallies and Great Locations 7 03-22-2011 09:57 PM
February '06 FMC Cover Story & Virtual Tour ikcandco Off-Topic Discussions & Humor 0 10-12-2006 08:10 AM

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Newell Coach Corporation or any of its affiliates. This is an independent, unofficial site.


All times are GMT. The time now is 02:47 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
×