Old 05-28-2008, 09:52 PM   #1
The Newell
Senior Member
 
The Newell's Avatar
 
Join Date: Dec 2005
Location: Southern California
Posts: 1,018
Default 12.5 KW Kohler Generator: How do I increase AC voltage?

The one on the drivers side will put out 120 volts.

The one on the passengers side only puts out 102 volts. When I increase the RPM's the voltage goes down.

Any thoughts? How does one go about increasing the AC voltage on a generator? I thought the speed increase would have helped.

BTW - I ran both AC units, turned on all of the 120v lights to see if the load would cause the Kohler to choke. It didn't miss a beat and kept putting out 102v. I only did this for 30 seconds as lower voltage will increase the amp draw of and could burn out an AC motor.
__________________

__________________
1976 Newell Classic (Sold)

Home Base: Riverside, CA

If anyone needs my contact info private message me and I will send it to you.

-Joseph-
The Newell is offline   Reply With Quote
Old 05-29-2008, 04:08 PM   #2
Richard and Rhonda
Senior Member
 
Richard and Rhonda's Avatar
 
Join Date: Oct 2007
Location: Huntington WV
Posts: 1,041
Default

Joseph,

This is indicative of a problem with the generator control circuits, or the windings themselves. The engines that drive the generators are governed at a certain speed to produce the 60 Hz alternating current. If you have played with the speed then you will need to adjust it back to get 60 hz.

Can you be more specific about the brand and model of genny.
__________________

__________________
Richard Rhonda Ty and Alex Entrekin
1995 Newell # 390 DD Series 60, Allison World Trans
Subaru Outback toad
CoMotion Tandem
Often wrong, but seldom in doubt
Rhonda's chronicle https://wersquared.wordpress.com/
Richard and Rhonda is offline   Reply With Quote
Old 05-29-2008, 04:18 PM   #3
fulltiming
Senior Member
 
fulltiming's Avatar
 
Join Date: Feb 2006
Location: Texas
Posts: 1,558
Default

Joseph, what are you basing the 102 volt reading on? If that is the reading on the voltage over the driver, you might also confirm that with a VOM to make sure the built in meter is working correctly. Does that meter show about 120 volts on that leg when the coach is plugged into shore power? Have you checked the frequency (Hz) of each of the two legs?

If the voltage is truly 102 volts on one leg, Richard is correct and you likely have a problem with the windings in the generator. The voltage should be VERY close between the two legs on power produced by the genset.
__________________
Michael and Georgia Day
1992 Newell 43.5' #281
8V92 DDEC-2, HT740
PT Cruiser GT with Remco Transmission Pump
https://newellowner.com/newell-photos/
fulltiming is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

» Recent Threads
No Threads to Display.
» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Newell Coach Corporation or any of its affiliates. This is an independent, unofficial site.


All times are GMT. The time now is 10:06 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
×